morphboy
Joined: 12 May 2005 Posts: 8
|
Posted: Sat Apr 19, 2008 11:55 am Post subject: Central Heating control valve problem |
|
|
With my central Heating on I find that the danfoss HSA3 valve will not go right over I have programmer danfoss cp715.
Below are voltages I find with CH(central heating radiators) and HW(hot water tank)
With CH and stat only on for heating then grey 240v,orange 0v, blue 0v,brown/white 240. Valve goes to mid position and nothing happens.
If I move valve to far side pump comes on and radiators are warming then grey 240v,orange 240v, blue 0v, brown/white 240v.
With HW on only and heating then grey 25v, orange 240v, blue 0v, brown/white 0v.
If HW on and heating then I add CH heating valve goes to mid position then grey 25v, orange 240v, blue 0v, brown/white 240v.
Any suggestions please? |
|
| Back to top |
|
 |
Whiter
Joined: 26 Jan 2003 Posts: 239
|
Posted: Sat Apr 19, 2008 7:10 pm Post subject: |
|
|
| Try a new valve head. |
|
| Back to top |
|
 |
morphboy
Joined: 12 May 2005 Posts: 8
|
Posted: Sun Apr 20, 2008 12:14 pm Post subject: |
|
|
I tried the actuator off the valve head and it worked ok, I found the mechanical/water diverter tight in places, I moved it backwards and forwards a number of times and everything works ok now , but as you suggest I will need to get another valve as it will probably tighten up again but it will be ok until I do.
Many thanks for the reply
Morphboy |
|