plumbingpages.com  
features news forums
e-mail   Search:
 

 
Primatic system

 


Post new topic   Reply to topic    PlumbingPages Forum Index -> Water Heating technical issues and questions
View previous topic :: View next topic  
Author Message
tim32



Joined: 29 Apr 2007
Posts: 4

PostPosted: Sat Dec 29, 2007 10:59 pm    Post subject: Primatic system Reply with quote

Hi I have with the help of my very good friend, changed our primatic cylinder to a standard indirect system, complete with f&e tank, however I am still finding that the upstairs rads are aproximatly two thirds full of air, and refuse to clear. The downstairs ones are no problem and work fine, one possible clue could be that when we try to bleed them the vent into the f&e tank returns some water.
any ideas would be appreciated
many thanks
Tim n(vgf) Jane
Back to top
View user's profile Send private message
tim32



Joined: 29 Apr 2007
Posts: 4

PostPosted: Fri Jan 04, 2008 4:26 pm    Post subject: further problems Reply with quote

Hi we have just got rid of the air, by means of putting a hose pipe onto the boiler drain and purging, this worked for a time, a very short time unfortunatly,
We found that as the heating system warmed up the water expanded and some left the system by means of the overflow, in the f&e tank.
When the system got switched off, cooled, and turned on again the water which had expanded and run off, was not replaced, and we have as much if not more air in the system.
The f&e tank is fairly low down, the bottom will be about the same height as the top of the upstairs rads, could it be that there is not enough pressure in the system to fill the rads, and if not is there anything that can be fitted to the system to sort it?
ta
Tim n Jane
Back to top
View user's profile Send private message
mark6266



Joined: 08 Feb 2003
Posts: 206
Location: sussex

PostPosted: Wed Jan 16, 2008 12:57 am    Post subject: Reply with quote

your f&e tank should be a least 1 meter above the highest point in the system
regards mark (allinplumbing@fsmail.net)
Back to top
View user's profile Send private message Send e-mail Visit poster's website
Display posts from previous:   
Post new topic   Reply to topic    PlumbingPages Forum Index -> Water Heating technical issues and questions All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
 



Template design by Skynet Design
Powered by phpBB © 2001, 2005 phpBB Group

Plumbing Courses | Site Map | Free Plumbing Advice | Plumbing News | Bathrooms | Showers | Plumbing | Bathroom Suites | Radiators | Taps | Sinks | Suppliers